Concrete introduction
This guide is designed around US procedures, with its:
- cold continental climate
- advanced technology
- preferential use of machines because of high labor costs
- easy access to quality materials
- research
- wealth
It follows that what is cheap and good quality in the US is not necessarily going to be cheap and good elsewhere.
Therefore this chapter is given, not as a recommendation of building materials, but for those who, having chosen concrete, want to understand the processes involved.
Index
Index:
- High quality slab
- Compact the subgrade
- Concrete cracks
- Water/cement ratio
- Concrete admixtures
- Curing concrete slabs
- Water-cure
- Control joints
- Three types of foundations
- The foundation construction process
High quality slab
High quality slabs require:
- compacted subgrade:
If the subgrade is not compacted and the ground becomes saturated after a good rain, the plumbing trenches under the house may collapse or the utility trenches connecting to the street may collapse under the driveway or other concrete flatwork. This would leave no support for the concrete.
If subgrade is built-up or 'filled-in', add 150mm then compact with heavy machine such as a digger, then add the next 150mm and compact, until desired level is reached.
In SE Asia, the subgrade for roads is rock, each piece about 150mm in diameter, placed firmly by hand. It is very successful, and probably more reliable than the 'western' method of compacting with a digger, but is cost-prohibitive in the 'west' because of high labor costs.
Do not use humus which can shrink with age as the molecules break down with microbial action. Do not use soil with a high clay content, particularly montmorillonite, a rose-red clay which expands and contracts with wetting and drying. This clay may be brown because of humus or other compounds. (Clay is my pet hate - cracking houses and destroying young trees - but I will master it yet.)
- level slab:
If the concrete is out of level (greater than 1 in 500 or 2mm in 1m) it causes expensive shimming or cutting of framing. If corrections are not made during framing, then lid lines may be noticeably out of level.
[Shimming: adding spacers/packing under the frame to lift it to the correct height.
Lid lines: where the wall meets the ceiling.]
- low water-cement ratio:
If the water/cement ratio is above 1/2 or 0.50 the concrete can be overly permeable causing:
- adhesives for vinyl flooring to loosen
- mold or mildew to form under vinyl
- vinyl to yellow
- grout in tile to become wet.
Excessive cracking can cause further problems with flooring materials and water permeation through the slab.
[Water-cement ratio is explained fully under its own heading, below.]
- vibrated concrete:
If the poured concrete is not properly vibrated the stiff concrete will contain large air bubbles and pockets. This greatly weakens the concrete and might cause leaks.
Mechanical vibration is the only way to fully remove air bubbles. Thorough tamping with poles, is much better than nothing but is still unsatisfactory. Worse still, it probably requires adding water to the mix before pouring, thus greatly weakening the concrete even further. You cannot tamp all the air out of concrete - it must be vibrated.
Too much vibration separates the sand, floating it to the surface and so weakening the concrete. Watch for tell-tale sand grains.
- floating or trowelling:
Floating or trowelling the surface is a skilled job, in order to have an effective but imperceptible slope. Every floor should drain water away from the walls to the doorway or, if inserted, to a drain in the floor (as in a workshop or bathroom). Yet in a house such a slope must be imperceptible to a visitor's eye.
In a house, the floor must also be smooth enough to lay tiles, without the expense of re-surfacing it.
- air entrainment in cold areas:
If air entrainment is not used in the mix in cold weather climates, water inside the concrete can expand when temperatures drop below freezing, and so fracture the concrete.
- control joints:
If control joints are not used with the proper spacing and placement, unsightly cracks can develop, leading to cracks in the vinyl or breaking tile grout.
- saddles:
Use plastic saddles or blocks to support the steel mesh in the slab. When pouring good-quality concrete, its stiffness and weight will press the mesh down to the plastic sheet underneath, instead of being vibrated through to enclose the mesh at the required 50-100m. This might widen any cracking, and so cause problems with flooring or water permeability.
Before plastic saddles were developed, we used a T-shaped piece of mesh with the bottom of the 'T' bent to form a hook. We used this to hook the mesh up off the plastic. It was impossible to get the correct distance off the plastic, and often, if there was even a brief delay, especially on a warm day, the concrete would stiffen too quickly to move the mesh.
Even with saddles, the weight of the stiff concrete will dip the mesh - be careful.
Consider using fibers in the concrete mix instead of steel mesh.
- curing:
If the concrete in not properly cured the concrete may develop cracks that would not otherwise have occurred. Proper curing delays the drying shrinkage until the concrete is strong enough to resist shrinkage cracking. Concrete which is moist cured for 7 days is about 50% stronger than concrete exposed to dry air for the same period.
Compacting the subgrade
All trenches should be compacted after filling:
- trenches under slab:
Excavations beneath the slab that are not to be filled with concrete (usually plumbing or other mechanical trenches) should be brought back to grade in compacted lifts. This means a 600mm trench would be backfilled 150mm at a time, each "lift" being mechanically vibrated so it is left compact.
If these excavations are not compacted when backfilled, this loose soil will settle over time leaving the concrete over that area with no earth under it. This becomes a prime place for concrete to settle. Since the soil next to these excavations is native soil, the uncompacted trench can literally become a thoroughfare for water.
- trenches under driveways:
Excavations from the house to the street for utilities should also be backfilled and compacted in the same manner so areas under the driveway concrete do not sink.
- trenches under lawns:
Uncompacted areas under lawns can be identified by areas of sunken grass; so compact trenches even under areas not receiving concrete.
Most rental yards have compacting equipment and it is worth the cost.
Concrete cracks
When installed properly, concrete is one of the most durable and long lasting products you can use around your home. But it is important that concrete contractors follow well-established guidelines with respect to concrete placement. Durable, high strength, and crack resistant concrete does not happen by accident.
Why concrete cracks:
- Excess water in the mix:
Concrete does not require much water to achieve maximum strength. But a wide majority of concrete used in residential work has too much water added to the concrete on the job site. This water is added to make the concrete easier to install. This excess water also greatly reduces the strength of the concrete.
Shrinkage is a main cause of cracking. As concrete hardens and dries it shrinks. This is due to the evaporation of excess mixing water. The wetter or soupier the concrete mix, the greater the shrinkage will be. Concrete slabs can shrink as much as 12mm per 30m. This shrinkage causes forces in the concrete which literally pull the slab apart. Cracks are the end result of these forces.
A low water/cement ratio is essential for concrete quality, and excess water reduces this quality.
What you can do about it:
Know the allowable water for the mix the contractor is pouring; or be very sure you have chosen a reputable contractor who will make sure the proper mix is poured. To do it right requires only a little extra manpower to pour stiffer mixes.
- Rapid drying of the concrete:
Rapid drying of the slab can also significantly increase cracking. The chemical reaction, which causes concrete to go from the liquid or plastic state to a solid state, requires water. This chemical reaction, or hydration, continues to occur for days and weeks after you pour the concrete.
You can make sure that the necessary water is available for this reaction by adequately curing the slab.
- Improper concrete-strength:
Concrete is available in many different strengths. Verify what strength your concrete should be, meazured in slump. To meazure slump when pouring, a little mix is packed into a container shaped like a plant pot, then inverted. When the container is slid upwards, leaving the mix 'upside-down', the concrete will slump. The wetter it is, the more it slumps. Building regulations specify the permissible amount of slump.
Talk to the ready mix supplier.
Consult with the Ready Mix Concrete Association in your area.
- Lack of control joints:
Control joints help the concrete to crack where you want. The joints should be 1/4 of the depth of the slab and no more than 24/1000 - 36/1000 times (in metres) of the thickness of the concrete (in millimetres). So 100mm concrete should have joints 2.4m - 3.6m apart.
- Other reasons:
Never pour concrete on frozen ground.
The ground upon which the concrete will be placed must be compacted.
The sub grade must be prepared according to your soil conditions. Some flatwork can be poured right on native grade. In other areas 150mm of base fill is required along with steel rebar installed in the slab.
Understand what your contractor is doing about each of the above listed items to ensure your concrete will be good quality.
Low water/cement ratio
Water/cement ratio must not be confused with water/dry-concrete-mix ratio. Although many people use the term 'cement' for what is concrete, cement is the gray powder which is added to sand and metal/aggregate, before mixing all together and then adding water.
Ratios are:
cement : sand : metal = 1:2:4 by volume roughly.
water : cement = 9:20 to 1:2 or between 0.45 and 0.5, by weight.
Try for less than 0.5 because even slight excess water rapidly ruins concrete.
Either use 1 kg of water = 1 litre;
and take the kilogram weight of cement in a mix, halve it, and call it litres of water.
or use 1 tonne of water = one cubic metre;
and take the tonne weight of cement, halve it and call it cubic metres of water.
That gives the upper limit of 0.5.
If you shift the decimal to get one-tenth, then subtract it, you get the lower limit of 0.45.
A low water/cement ratio is the major factor for good concrete.
A low water/cement ratio is essential for all the desired properties of concrete.
And yet, the truckie who delivers your concrete will probably have added water to your concrete, without your permission, so it pours down his truck's chute easily. Or sloshes about easily in his truck's drum. Whatever the reason, he does not care about the quality of your concrete. I have yet to see concrete delivered without excess water in it. When you walk over concrete slabs, check the excess cracking which results.
A guide to water/cement ratios is:
- Use the maximum 0.50 water/cement ratio when:
- concrete is exposed to freezing and thawing in a moist conditions
- de-icing chemicals are added.
- Use a maximum 0.45 water/cement ratio for concrete with severe or very severe sulfate conditions.
- Never use water/cement > 0.5. Water permeability increases exponentially when water/cement ratio is greater than 0.50.
- Durability increases as the concrete mix becomes less permeable.
- Strength improves with lower water cement ratios, increasing by about 10% as water/cement drops from 0.5 to 0.45.
For complete Building Code information regarding concrete construction, review with your architect, your ready mix supplier, or at your local library.
Curing concrete slabs
Why cure concrete?
Curing serves two main purposes:
- it retains moisture in the slab so that the concrete continues to gain strength
- it delays drying shrinkage until the concrete is strong enough to resist shrinkage cracking.
Properly curing concrete improves:
- strength
- durability
- water tightness
- wear resistance.
How to cure concrete:
- Water-cure: the concrete is flooded, ponded, or mist sprayed. It is the most effective curing method for preventing water evaporation from fresh concrete.
- Water retaining methods: use coverings such as sand, canvas, burlap, or straw that are kept continuously wet. The material used must be kept damp during the curing period.
- Waterproof paper or plastic film seal: These are applied as soon as the concrete is hard enough to resist surface damage. Plastic films may cause discoloration of the concrete, so do not apply to concrete where appearance is important.
- Chemical Membranes: the chemical application should be made as soon as the concrete is finished. Note that curing compounds can effect adherence of resilient flooring; so your flooring contractor and/or chemical membrane manufacturer should be consulted.
All the desirable properties of concrete are improved by proper curing.
Water-cure
After concrete is placed, the concrete increases in strength very quickly for a period of 3-7 days. Concrete which is moist-cured for 7 days is about 50% stronger than uncured concrete.
Water-curing can be done after the slab pour by building dams with soil around the house and flooding the slab. The enclosed area is continually flooded with water. Ideally, the slab could be water cured for 7 days. Some builders on a tight schedule water cure for 3 days as this achieves approximately 80% of the benefit of water-curing for 7 days.
Consider planning your job to pour at the end of the week, build berms, then flood over the weekend. You get the benefit of water-curing without losing too much time in the schedule.
Control joints
Be active in deciding where control joints will be placed.
Control joints are planned for cracks which allow for movements caused by temperature changes and drying shrinkage. In other words, if the concrete does crack-you want to have an active role in deciding where it will crack and that it will crack in a straight line instead of randomly.
Space joints properly. Space joints (in metres) no more than 24/1000 - 36/1000 times the slab thickness (in mm). A 100mm slab should have joints 2.4m - 3.6m apart.
Cut joints deep enough. Cut joints 25% of the depth of the slab. A 100mm thick slab should have joints 25mm deep.
How to cut joints.
Grooving tools cut joints in fresh concrete. Saw cutting cuts joints as soon as the concrete is hard enough that the edges abutting the cut do not chip from the saw blade.
Cutting joints soon enough. In hot weather, concrete might crack if joints are not cut within 6-12 hours after finishing concrete. In this condition, if you do not want to use a grooving tool to cut joints, there are early-entry dry-cut lightweight saws that can be used almost immediately after finishing. These saws cut 25mm to 75mm deep, depending on the model.
Place joints under walls or under carpet areas. Under walls they won't be seen. Under carpet areas the joints won't have a chance to telegraph through vinyl areas.
Avoid re-entrant corners. Planning the joint pattern can sometimes eliminate re-entrant corners.
Note: Inside corners, where cracks would typically occur, have correctly placed joints.
Most plans do not have joint spacing marked on them, so do not leave this important part of concrete construction to chance.
Jointing is often not taken seriously enough and the "sawcutter" comes to your job and puts the cuts where he feels they belong or where it is convenient for him.
Be active in deciding where control joints will be placed!
Three types of foundations
The 3 types of foundations are:
- T-Shaped
A traditional foundation method to support a structure in an area where the ground freezes. A footing is placed below the frost line and then the walls are added on top. The footing is wider than the wall, providing extra support at the base of the foundation:
- T-shaped foundations are used in areas where the ground freezes.
- First, the footing is placed
- Second, the walls are constructed and poured
- Lastly, the slab is placed.
- Slab-on-grade foundation
As the name suggests, a slab is a single layer of concrete, several inches thick. The slab is poured thicker at the edges, to form an integral footing; reinforcing rods strengthen the thickened edge. The slab normally rests on a bed of crushed gravel to improve drainage. Casting a wire mesh in the concrete reduces the chance of cracking. A slab on grade is suitable in areas where the ground does not freeze, but it can also be adapted with insulation to prevent it from being affected by the frost heaves. (see below)
In summary:
- Slab on grade used in areas where ground does not freeze.
- The edges of the slab-on-grade are thicker than the interior of the slab.
- The slab-on-grade is monolithic (poured all at one time).
- Frost Protected
This method only works with a heated structure.
To prevent freezing, which is a problem with slab-on grade foundations in areas with frost, it relies on the use of two sheets of rigid, polystyrene insulation:
- one on the outside of the foundation wall
- the other laid flat on a bed of gravel at the base of the wall
The insulation holds heat from the structure in the ground under the footings and prevents heat loss from the edge of the slab. This heat keeps the ground temperature around the footings above freezing.
In summary:
- Only works with a heated structure.
- Has the benefits of a the slab-on-grade method (concrete poured monolithically) in areas subject to frost.
- Concrete is poured in one operation, versus 3 pours required for T-shaped foundations.
The foundation construction process
Listed here is the foundation construction process:
- Week 1
Ground breaking, excavation
- Grading the lot and getting it tested for compaction
- Digging trenches for footings
- Setting batter boards to level the house
- Week 2
Footings dug, rebar set, inspection, footings poured
- Installing rebar (and using safety caps)
- "Boom pumping" concrete
- Week 3
Stem wall forms, stems poured, rough-in plumbing
- Installing polystyrene blocks for pouring insulated stemwalls. Cold migrates into the home through the stem walls and slab if the stemwalls are not insulated.
- Week 4
Radiant heat, inspection, poured slab:
- The ground inside forms is prepped for the slab
- Plumbing pipes are run under the ground and stubbed up in their exact locations
- Black plastic is laid on the ground as a radon shield
- Plastic tubing is laid for the radiant heat. The location and density of the tubes correspond with the space it will be heating and the finish flooring to be used.
- The concrete is "boom pumped" into place
- Week 5
Clean-up, site grading, block wall
The site is cleaned up and prepared for the framing crew.