Shocking plumbing

From an Australian government source:
http://www.actpla.act.gov.au

Avoid electrical shocks when working with water supply mains.

Electrical shocks are a risk for plumbers when they change water meters and other equipment in residential and commercial buildings.
Because of the risk, it is essential to use bridging devices such as heavy duty jumper leads to bridge plumbing gaps:

How faults occur

Installing plastic water pipes on the street mains side of the water meter reduces the length of conductive water pipe connected to an electrical installation main earthing system. When plastic water pipe is added, it may introduce insulated sections in the water mains network.  This creates a water mains system that becomes ineffective as an electrical earth return pathway to a local substation, resulting in a higher shock risk. This electrical shock risk is higher in residences in older Canberra suburbs built in the 60s and 70s where original pipes were copper and cast iron.

With the transition from metallic to plastic mains water reticulation, the risk of shock is greater at a temporary plumbing gap during the removal and replacement of a water meter or valve. A shock risk may exist at this changeover point if an electrical fault develops at the same address.

It is common for neutral wiring to become ineffective due to the many overhead and underground cable joints that exist in the ActewAGL distribution network. The electrical installation's main earth and neutral bond are made at the main neutral link within the residence or commercial switchboards.  This bond in older suburbs may still rely on metallic water pipes for electrical earthing.

Danger of electric shock

If the service neutral wire is faulty, any fault current will be conveyed to the substation via the earthing system and nearby water mains rather than by the service neutral.  As a result, voltages up to 240 volts can develop between:
When the metallic water pipe is in contact with soil and clay along its entire length, the resistance to electrical current flowing back to the substation is low and the voltage is proportionally lower and less severe if contacted across hands or hand to feet. 

When electrical current from a faulty neutral condition is conveyed to metallic piping but is interrupted by the introduction of new plastic piping and there is no earthing electrode to convey fault current to the soil mass, a dangerous shock risk may exist to:
If the metallic water pipe system within a premises is continuous, it provides an effective contact with the earth and clay mass. If earth leakage current exists within the house’s wiring and the metallic water pipes are no longer electrically continuous through recent changeovers to plastic piping, it is probable that an electrical shock risk could arise.

For example, when a tap connected to what was a continuous metallic water pipe earth system becomes ineffective, it is more likely that a voltage difference will arise between the tap and the exposed parts of household drainage.  A fault current can flow through a person who is making simultaneous contact with the energised tap handle and any drainage point. The combination of very small electrical current and voltage can cause dangerous electrical shock, particularly in damp situations. For plumbers, the higher the fault current and voltage, the greater risk of electrocution if in contact across gaps in metal piping and surrounding soil.

A licensed electrician, with the help of ActewAGL’s network operator, can detect and remove electricity on plumbing piping generally due to a neutral fault.

Reduce the risk

Before starting plumbing work:
If any test reveals a voltage of more than 5 volts alternating current and it is a constant value it is deemed a dangerous voltage. Please note that voltages in the low range of 240 volts are a serious shock risk. (It is not the voltage that kills, but the current and that need only be small.)

Plumbers are trained during their apprenticeship to connect bonding cables, typically battery jumper leads, across the water pipe point to be breached before all work is started.
Take care not to touch the metal piping and other adjacent structural metallic parts when connecting a plastic water pipe or insulated meter or standard fittings to any part of the plumbing.

All construction trades are warned that installed metallic water pipe work may have an electrical hazard if a tradesperson makes physical contact across gaps in metallic pipes and to adjacent structural metal or damp surfaces. 
The water pipe gap must be tested prior to the start of work. Call a licensed electrician to isolate supply.  (We should all note that this threat is deemed so serious that all electricians in the ACT must contact ActewAGL and inform them of the electrical risk.)

To maintain a safe electrical installation, reinstate and paint all electrical earth bonds that were temporarily removed from metallic piping during plumbing after work is completed.
Plumbers must always reconnect a main earthwire to an earth electrode using the same safety principles applied to a pipe breach.

Warning for older homes

In central Canberra residences, the metallic water pipe has a main earth connection at the point of mains water entry into the residence unless it has been significantly refurbished.
This is one of the essential connections for the electrical earthing system.

This system is now out-dated and all installations that are upgraded due to building refurbishment or extension must have an earth stake (electrode) installed whenever new circuits are created or an electrical installation switchboard is replaced.

Plumbers may need to engage a licenced electrician to explain to their customer who is having plumbing upgrades, that changes to waterpipes may affect the electrical installation and its main earthing system.  The plumber’s electrician should recommend to the homeowner that the inclusion of a safety switch (residual current device (RCD) or safety switch) on existing electrical installation light and power circuits improves electrical safety.
However, electrical safety depends on modern installation earthing principles and practice.