Household water

Edited from Wikipedia (October 2011)
PT.org thanks Wikipedia especially for the section on Tap versus bottled water.

Household water was a key factor in the reduction of disease from about 1870 - 1970. Towards the end of the 20th century, commercially bottled water has made significant inroads into the use of household water for drinking, even though commercially bottled water can be noticeably impure and its health claims merely false advertising propaganda.

One French bottling company was importing its 'spring' water from our island, halfway around the world, and marketing it internationally, when analysis showed that the expensive bottled water sold to the wealthy, contained possum faeces. (Knowing where the water came from, we could have told them that, but nobody bothered to ask.)

Contents

Background
Potable water supply
Hot water supply
Fixtures and appliances
Pipe materials
Steel
Copper
Sizes
Lead leaching
Corrosion
Pin holes
Danger of electric shock
Plastics
Fittings and valves
Regulation and compliance
Waste water
Tap water versus bottled water
Dissolved gases

Background

Governments take responsibility, either directly by themselves or through private companies, for the provision of filtered and chemically treated water,in order to vastly reduce epidemics of water-borne diseases, such as cholera (often transmitted by faeces in underground water). The pipework from treatment plant through the suburbs and into your home is called reticulated water system.

The water coming to you is far from pure.Your tap water is filtered but this removes only large particles, not dissolved chemicals. Your water may contain:
In spite of government efforts, tap water can be contaminated biologically or chemically, whence governments might advise the public:

This supply may come from several possible sources:
Modern reticulated water systems provide all households with water for at least cooking and cleaning, and most guarantee satisfactory drinking water. Similarly the waste water (graywater and sewage) is also a self-contained or isolated reticulated system. Since the incoming water and the outgoing waste are isolated from each other by their own reticulated systems, there is no cross-contamination, unlike the 19th century practices that caused deadly epidemics, by such diseases as cholera.

Fixtures and appliances

Everything in a building that uses water falls under one of two categories: Both fixtures and appliances produce waste/sewage components that will require removal by the waste/sewage side of the system. All of them each requires a U-bend before exiting the room, where the U-bend holds water to prevent the backflow of gases which develop in graywater and sewage pipes.

Hot water supply

Domestic hot water is provided by household electric, gas, wood, or solar heaters, or through district heating which may include thermal springs.

Pipe materials

Evolution of the pipe: Plastic supply pipes have become increasingly common, with a variety of materials and fittings employed. However plastic water pipes do not keep water as clean as copper and brass piping do. Copper is bacteriostatic, meaning that bacteria cannot grow in copper pipes.

Plumbing codes define which materials may be used, and all materials must be proven by ASTM, UL, and/or NFPA testing.

Steel

Galvanized steel potable water supply and distribution pipes are commonly found with nominal diameters from 3/8" to 2". It is rarely used today for new construction residential plumbing.

Steel pipe has National Pipe Thread (NPT) standard tapered male threads, which connect with female tapered threads on elbows, tees, couplers, valves, and other fittings.
Galvanized steel (often known simply as "galv" or "iron" in the plumbing trade) is relatively expensive, difficult to work with due to weight and requires a pipe threader.
It remains in common use for repair of existing "galv" systems and to satisfy building code non-combustibility requirements typically found in hotels, apartment buildings and other commercial applications. It is also extremely durable. Black lacquered steel pipe is the most widely used pipe material for fire sprinklers and natural gas.

Most single family homes' systems typically won't require supply piping larger than 3/4". In addition to expense, another downside is it suffers from a tendency to become obstructed by internal rusting and mineral deposits forming on the inside of the pipe over time after the internal galvanizing zinc coating has degraded.

In potable water distribution service, galvanized steel pipe has a service life of about 30 to 50 years, although it is not uncommon for it to be less where water contains corrosive compounds.

Copper sizes

Common wall-thicknesses of copper tubing in the USA are:
Types K and L are generally available in both hard drawn "sticks" and in rolls of soft annealed tubing, whereas type M is usually only available in hard drawn "sticks".

In the US plumbing trade the size of copper tubing is measured by its nominal diameter (average inside diameter). In contrast, some American trades, such as heating and cooling technicians, use the outside diameter (OD) to designate copper tube sizes. The HVAC tradesman also use OD to separate copper pipe for airconditioning, which has not been treated with processing oils incompatible with the lubricants in AC compressors.

The OD = ND + 1/8" (= average ID + 1/8") Therefore, 1" nominal copper tube and 11/8" ACR tube are the same tube with different size designations. The wall thickness of the tube, as mentioned above, never affects the sizing of the tube. Type K + 1/2" nominal tube, is the same size as Type L 1/2" nominal tube (5/8" ACR).

Common wall-thicknesses in Europe, defined by the EN-1057 standard, are: 
In the Australian plumbing trade the size of copper tubing is measured by its outside diameter in millimetres. Common sizes are 15 mm and 22 mm.

Thin-walled types used to be relatively inexpensive, but since 2002 copper prices have risen considerably due to rising global demand and a stagnant supply.

Lead leaching

Generally, copper tubes are soldered directly into copper or brass fittings, although compression, crimp, or flare fittings are also used. Formerly, concerns with copper supply tubes included the lead used in the solder at joints (50% tin and 50% lead).

Some studies have shown significant "leaching" of the lead into the potable water stream, particularly after long periods of low usage, followed by peak demand periods. While lead chloride is also fairly insoluble in cold water, in hot water it becomes very soluble.

In hard water applications, shortly after installation, the interior of the pipes will be coated with the deposited minerals that had been dissolved in the water, and therefore the vast majority of exposed lead is prevented from entering the potable water.

Building codes now require lead-free solder. Building Codes throughout the U.S. require the use of virtually "lead-free" (<0.2% lead) solder or filler metals in plumbing fittings and appliances as well.

In buildings old enough to have been plumbed with lead solder (as late as the 70s and possibly the 80s) you should avoid the common habit of using water from the hot tap, for drinking and cooking purposes. Nobody will keel over and die, because the effects of lead poisoning are slow and subtle, such as brain damage.

Corrosion

Copper water tubes are susceptible to:

Pin holes

Pin holes due to poor plumbing electrical grounding and/or bonding Pin-hole leaks can occur where copper piping is improperly grounded and/or bonded. Non-metal piping, such as Pex or PVC, does not suffer from this problem. The phenomenon is known technically as stray current corrosion or electrolytic pitting.

Pin-holing, due to poor grounding or poor bonding, occurs typically in homes where the original plumbing has been modified; homeowners may find a new plastic water filtration device or plastic repair union has interrupted the water pipe's electrical continuity to ground when they start seeing pinhole water leaks after a recent install.

Damage occurs rapidly, usually being seen about six months after the ground interruption. Correctly installed plumbing appliances will have a copper bonding jumper cable connecting the interrupted pipe sections.

Pinhole leaks from stray current corrosion can result in thousands of dollars in plumbing bills, and sometimes necessitating the replacement of the entire affected line. The cause is an electrical problem, not a plumbing problem; once the plumbing damage is repaired, an electrician should be consulted to evaluate the grounding and bonding of the entire plumbing system.

The difference between a ground and a bond is subtle. See Ground (electricity), find the heading AC power wiring installations for a complete description.

Stray current corrosion occurs because: The DC voltage forces the water within the piping to act as an electrical conductor (an electrolyte). Electric current leaves the copper pipe, moves though the water across the nonconductive section (the plastic filter housing in the example above), and reenters the pipe on the opposite side.

Pitting occurs at the electrically negative side (the cathode), which may be upstream or downstream with respect to the water flow direction. Pitting occurs because the electrical voltage ionizes the pipe's interior copper metal, which reacts chemically with dissolved minerals in the water creating copper salts; these copper salts are soluble in water and wash away.

Pits eventually grow and consolidate to form pin holes. Where there is one, there are almost certainly more.

Detecting and eliminating poor bonding is relatively straightforward. Detection is accomplished by use of a simple voltmeter set to DC with the leads placed in various places in the plumbing. Typically, a probe on a hot pipe and a probe on a cold pipe will tell you if there is improper grounding. Anything beyond a few millivolts is important. Potentials of 200 mV are common.

A missing bond will show up best in the area of the gap, as potential disperses as the water runs. Since the missing bond is usually seen near the water source, as filtration and treatment equipment are added, pinhole leaks can occur anywhere downstream. It is usually the cold water pipe, as this is the one that gets the treatment devices.

Correcting the problem is a simple matter of either purchasing a copper bonding jumper kit, composed of copper cable at least #6 AWG in diameter and two bronze ground clamps for affixing it the plumbing. See NFPA 70, the U.S. National Electrical Code Handbook (NEC), section on bonding and ground for details on selecting the correct bonding conductor wire size.

A similar bonding jumper wire can also be seen crossing gas meters, but for a different reason.

Danger of electric shock

If homeowners are experiencing shocks or sparks from plumbing fixtures or pipes, it is more than a missing bond; it is likely a live electrical wire is bridging to the plumbing and the plumbing system is not grounded. This is an electrical shock hazard and potential fire danger; consult an electrician immediately.

In Australia the electrical system used to be earthed to the copper reticulation which is in turn grounded to a standard copper rod of about 10mm diameter driven a metre into the ground. Check that both these connections are still intact.

Then check why the green wire connection to the copper pipes, is alive. All green wires must lead eventually back to the bus bar in the metre box, and this bar is connected to the neutral black or brown wire which is the neutral for all your electrical wiring. If the green wire to the pipe is alive, then it is likely that someone, at the time that the water became electrified, has fiddled with the wiring in an appliance or a socket. Ask: Failing that, the neutral wire in the meter box, might not be neutral; read the next paragraph.

If the service neutral wire is faulty, any fault current will be conveyed to the substation via the earthing system and nearby water mains rather than by the service neutral. 
As a result, voltages up to 240 volts can develop between:
Above all, see the chapter Shocking plumbing for a government warning with appropriate procedure.

Fiddling with electrics is a life-threatening pastime – even electricians get electrocuted. (When a home handyman electrocuted himself, they checked his wiring and found 8 dangerous mistakes. Obviously he thought he could do electrics; but unfortunately did not know enough to realize how little he knew.)

An electrician is cheaper than a mortician.

Plastics

Plastic pipe is widely used for domestic water supply and drainage, waste, and vent (DWV) pipe:
These may be allowed by code for certain uses.
Some examples of plastics in water supply systems are:

Fittings and valves

Potable water supply systems require not only pipe, but also many fittings and valves which add considerably to their functionality as well as cost.

Regulation and compliance

Before a water supply system is constructed or modified, the designer and contractor need to consult the local plumbing code and obtain building permits prior to construction. Even replacing an existing water heater may require a permit and inspection of the work. NSF 61 is the U.S. national standard for potable water piping guidelines. National and local fire codes should be integrated in the design phase of the water system too to prevent "failure comply with regulations" notices. Some areas of the United States require on-site water reserves of potable and fire water by law.

Waste water

The waste water from the various appliances, fixtures, and taps is transferred to the waste (graywater) and sewage removal system via the sewage drain system. This system consists of larger diameter piping, water traps, and is well vented to prevent toxic gases from entering the living space. The plumbing drains and vents article discusses the topic further, and introduces sewage treatment.

There must always be a U-bend inside the house connecting to the outlet from the house, such as between the sink, shower, washing and dishwashing machines, and toilet, and the exit pipes to the graywater and sewage pipes. The U-bend keeps a reserve of water in the bend to stop gases from the graywater and sewage, coming into the house. In San Pedro, Chile, I saw a handyman install a laundry sink in the courtyard of a hotel, without a U-bend, and the whole hotel reeked of sewage.

Tap water versus bottled water

(This is from Wikipedia, quoted without comment.)
The examples and perspective in this section may not represent a worldwide view of the subject.

In modern Western society, levels of contaminants found in tap water vary for every household and plumbing system. A general conception regarding water is that bottled water is designed to be 'cleaner' than conventional tap water.
However, in 1999, The Natural Resources Defense Council (NRDC) released controversial findings from a four year study on bottled water. The results of this study claimed that one-third of the waters tested contained levels of contamination – including synthetic organic chemicals, bacteria, and arsenic – in at least one sample that exceeded allowable limits under either state or bottled water industry standards or guidelines.
However, the bottled water industry was quick to dispute the claim saying bottled water is one the most highly regulated food products under the FDA regulatory authority and that the FDA system worked extremely well when coupled with the International Bottled Water Association's Model Code and unannounced inspections.

Some municipalities in the United States are making an effort to use tap water over bottled water on government properties and events. However, others voted the idea down, including voters in the state of Washington who repealed a bottled water tax via citizen initiative.

James Workman, author of the book Heart of Dryness: How the Last Bushmen Can Help Us Endure the Coming Age of Permanent Drought and co-founder of SmartMarkets says that he doesn't believe that "tap water is bad and bottled water is good". Rather he cites differences in quality regulations and standards. "Bottled water is often tap water put through another filter and not held to the same quality regulations as public utility water is."

Chlorine is a disinfectant which is added to tap water in the United States. Chlorine can leave organic material like trihalomethanes and haloacetic acids in the water. The level of chlorine found is small, 1L of chlorinated water gives 0.2 mg of chlorine, which is too small to cause any health problems.

While most U.S. cities have what is considered safe tap water, contaminants ranging from bacteria to heavy metals are present in some tap water and violations of tap water standards have been well-publicized, such as the severe 1993 Cryptosporidium outbreak in Milwaukee, Wisconsin, which led to several deaths and around 400,000 illnesses (see: Milwaukee Cryptosporidium outbreak). The University of Cincinnati recently completed a Tap Water Quality Analysis, funded by PUR, for major US cities.

Dissolved gases

Tap water can sometimes appear cloudy, and this is often mistaken for a mineral impurity in the water. Cloudy water, also known as white water, is actually caused by air bubbles coming out of solution in the water. Because cold water holds more air than warm water, small bubbles will appear in water with a high dissolved oxygen content that is heated or depressurized, because this reduces how much dissolved gas the water can hold. This condition is completely harmless, and the cloudiness of the water disappears quickly as the gas is released from the water.