Hot water installation
It is recommended:
- Fittings for inserting in water circuit:
- Expansion control valve
- In line non-return valve
- Isolating valve
- Cold water supply line
- Line strainer
- Pressure limiting valve
- Requirements
that the
system
be installed in accordance with the manufacturers
installation requirements, AS/NZS 3500 Part 4 and
any local by-laws with particular reference to the
pressure and temperature relationship as described
in AS / NZS 2642 and detailed in Table 1.4.
- Temperature-pressure
The valves used in the installation of water heaters
should comply with the requirements as laid out in
AS/NZS 3500 Part 4, Tables 4.1 & 4.2.
The required set pressure of valves i.e. expansion
control valves and inlet pressure control valves
shall be:
- as specified by the water heater manufacturer, or
- determined from the set pressure of the
temperature and pressure relief valve supplied
by the water heater manufacturer, with reference
to AS/NZS 3500 Part 4, Table 4.2.
Pressure rating of pipes according to pipe material
temperature (AS 2642)
Working temp oC | Working Pressure kPa |
20 40 50 60 70 80 |
1600 1370 1200 1050 880 740 |
- Tempering valves
The use of tempering valves is required in some
capital cities and provincial areas. Check with your
Local Authority.
- Thermostat
The water heater thermostat must be set to supply
hot water at temperatures less than 80°C.
Please note:
In accordance with AS/NZS 3500 Parts 1 & 4, copper
pipe should be used within one metre of the outlet of a
hot water heater.
Before connecting PB to instantaneous gas hot water
systems, check with the hot water heater manufacturer
for any specific additional requirements.
PB should not be used in continuously circulating hot
water plumbing loops operating above 60oC.