Polybutylene Plumbing System Installation Guidelines
Equipment and materials:
- Crimping tool with caliper gauge
- Flexible Polybutylene (PB) pipe
- 18mm & 22mm x 5m lengths
- 25m or 50m coils
- DR brass fittings with copper crimp sleeves.
No brazing; no gas bottles; no torches, filler rods, or fluxes, except for brazing tails to connect copper pipe
or metal fittings to PB pipe.
Intro
This technical manual details features and installation
aspects of the three ranges of
Polybutylene (PB) pipes and fittings system:
- Hot and Cold Water
Grey PB Pipe, coloured
grey to inhibit fungal growth in the potable water within
the pipe.
- Recycled Water
Purple PB Pipe, carrying the print message WARNING:
RECYCLED OR RECLAIMED WATER - DO NOT DRINK.
This product can be used when a second non-potable
water supply is available for toilet flushing etc.
- Rain Water I
Green PB Pipe, carrying the print message
RAINWATER, developed to connect
your rainwater tank to household appliances, including
washing machines and toilet cistern.
Fittings and tools for all three pipe systems are identical.
The system meets the requirements of
Australian Standard AS/NZ 2642 Parts 2 & 3, and
is intended for use by licensed plumbing tradesmen who
work to the Australian/New Zealand
National Plumbing and Drainage Standard AS/NZS 3500.
This system is:
- flexible enough to
be bent by hand
- extremely light weight
- corrosion resistant
- eliminates water hammer noise
- withstands
high pressures and temperatures.
In particular, no brazing or soldering is necessary except for the 1-metre of copper pipe coming from the outlet of the hotwater cylinder (in accordance with AS/NZS 3500 Parts 1 & 4).
When
installed by a licensed tradesman, the system has proven
to be both high quality and economical to use.
(However, see last paragraphs on insurer's comments.)
Polybutylene pipe must be physically protected from direct
sunlight to avoid long term UV degradation.
The system
This system uses:
- Fittings
The
PB pipes and fittings system
has a comprehensive range of fittings that are suitable
for general plumbing use. Installation instruction leaflets must be followed.
- DR Brass Fittings
Brass that
is not resistant to dezincification can lose its zinc content
leaving a residue of spongy or porous copper.
Some brass fittings are fully resistant to dezincification, in accordance with AS2345. Such brass contains less than 15% zinc, or has been heat
treated or chemically enhanced to make it resistant to
the loss of zinc. These brass fittings can be used in the ground in
most situations.
- Copper Crimp Sleeves
The brass fittings have an annealed
copper crimp sleeve with a pipe depth insertion
window to provide visible assurance that the pipe has
been pushed fully home.
-
Dimensions of PB pipe
| NOD ** | Mean bore |
18 mm 22 mm |
12.5 mm 17.6 mm |
** NOD = nominal outside diameter
In accordance with AS/NZS 2642 Class 16.
- Dimensions of fittings
| Class. | NOD ** | Mean bore |
DN18 DN22 |
18 mm 22 mm |
9.0 mm 14.5 mm |
** NOD = nominal outside diameter
- Crimping Tools
Care should be taken to ensure
that moving parts are not damaged. Caliper gauges are supplied with all tools to check that
the copper ring has been properly crimped.
Advantages
Some of the advantages are:
- Light weight and flexible - for ease of assembly.
- Simple jointing system - quick assembly, high integrity.
- No brazing, soldering, gases, silver solders or fluxes.
- No electrolysis.
- Corrosion resistant - for aggressive conditions.
- Long lengths, therefore less joints and fittings - for
ease of assembly.
- Eliminates water hammer noise - reduced call backs.
- Little resale value - minimises theft.
- Tamper proof jointing system - once the system is
crimped it cannot be pulled apart.
Disadvantages
Disadvantages:
- Polybutylene pipe must be physically protected from direct
sunlight to avoid long term UV degradation.
- PB should not be used in continuously circulating hot
water plumbing loops operating above 60oC.
- In accordance with AS/NZS 3500 Parts 1 & 4, copper
pipe, not PB, should be used for the first one metre of the outlet of a
hot water heater. Check the wording of this regulation.
- Extra care must be taken of PB pipe to avoid wastage.
Do not use pipe which has:
- cuts, deep scratches or gouges
- Kinks or crushed sections
- Evidence of grease, oil, tar etc.
- Noticeable colour fading of pipe.
All damaged sections should be cut
out and replaced.
- Abide by the limitations of PB pipe.
Avoid using:
- as part of a water meter assembly or vertical
riser
- beyond the inlet stop valve to any water heater
- where subject to direct sunlight
- in areas subject to contamination by
petroleum products
- within one metre of the outlet of, or between
isolation valve and inlet of any water heater
- where water temperature / pressure combinations might exceed the limitations as given by the manufacturer
- on continuously circulating hot water loops
operating above 60oC
- buried underground and subject to flooding with a
termite treatment.
Before installation
Pre-installation:
- Store PB pipe under cover where
it will not be exposed to direct
sunlight.
- Do not use pipe which has:
- cuts, deep scratches or gouges
- Kinks or crushed sections
- Evidence of grease, oil, tar etc.
- Noticeable colour fading of pipe.
All damaged sections should be cut
out and replaced.
Jointing
Crimped connections:
- Cut pipe squarely with the PBcutter. Do not use a hack saw.
- Slide the pipe onto the fitting until it stops. If
fitted correctly, the pipe should be visible through both
the copper crimp sleeve windows.
- Ensure that the copper crimp sleeve is firmly attached to
the plastic retainer ring. If the copper crimp sleeve has
moved away from the plastic retainer ring, push it back
onto the plastic retainer ring by hand before crimping.
- Open crimp jaws all the way apart. Position crimp
jaws squarely over the copper crimp sleeve, that is, at 90o to
the pipeline.
- For hand tools ensure that the full jaw width
of the tool makes contact with the copper crimp sleeve
when crimping.
- For power tools crimp the jaws over the
full width of the copper crimp sleeve.
- Avoid crimping the
plastic retainer ring.
- Close the crimp tool jaws fully over
the copper crimp sleeve.
- Open the crimp tool jaws and
remove the crimp tool from the crimped fitting.
- Use the caliper gauge supplied with the
tool to check each and every joint. Gauge tips must fit
over the crimped copper sleeve at 90o to the tool jaw
split line.
The tools have to be
protected against dirt and damage, and should be
cleaned regularly.
Faulty connections
The fitting technique is simple
and effective when executed in accordance with
the jointing procedures. However, lack of care can cause improper sealing with a potential for leaks.
The most likely causes of faulty connections are:
- Under-crimping (which will be shown when the caliper gauge will not pass over
copper ring) can occur when:
- the crimping tool has not been completely closed
- The crimping tool is out of adjustment
(readjustment should be made in accordance with
the instructions supplied with the tool)
- copper crimp sleeve has moved away from the
body of the fitting
- the crimping tool has not been centred over the
copper crimp sleeve, and thus the sleeve has only
been partially crimped
- the pipe has not been pushed fully home on to the
fitting when the crimp was made
- pipe has not been cut squarely
- Tools are poorly maintained or damaged.
If an incorrect joint is detected, cut out the defective joint and replace with new fitting
If the pipe is kinked or damaged, the faulty section of the pipe should be replaced.
PB to copper/steel pipes
Metal threaded fittings, such as brass or copper,
should not be used with non-metal threaded
fittings.
Use an approved sealant to seal all threaded
fittings.
When using brazing tails to connect copper pipe
or metal fittings to PB pipe, always
braze the brazing tail to the copper pipe or metal
fittings first and allow it to cool before assembling the PB pipe.
At least four ribs should be shown on the brazing tails to
allow for an effective joint to be made. It is
recommended that silver brazing alloys be used and
that all flux deposits are removed once the joint has
been made.
Excessive heat can damage
PB pipes. When brazing copper pipes or fittings near PB pipes it is recommended a damp rag
be used to protect the pipes.
Pipe bending
Due to the pipe’s inherent flexibility and its availability
in 50m coils for 18mm and 22mm pipe, polybutylene
can be bent easily around obstructions or through studs
and plates with minimum use of fittings. Care should be
taken not to kink or damage the pipe. It is
recommended that the minimum bending radius be 10
times the outside diameter of the pipe. If this is not
possible an
elbow should be used. If for
any reason the pipe is kinked or damaged, the faulty
section should be replaced.
Minimum bending radius OD x 10:
- 18mm Pipe: 180mm minimum radius
- 22mm pipe: 220mm minimum radius
PB inside structures
When placing PB pipe inside the framework and slabs of buildings:
- Timber framework
Holes drilled in studs or plates etc. shall be accurately
sized to allow longitudinal movement of the pipe
through the hole with a minimum clearance of 2mm on
the pipe’s diameter. A 25mm splade bit is suitable for
both sizes of pipe. Please note that the use of silicon in
the holes is not required.
- Metal framework
Holes drilled in metal studs or plates etc shall be
accurately sized to enable suitable grommets, lagging or
a short sleeve of oversized pipe to be firmly secured in
the framework. This is to allow free movement of the
pipe through the grommet, lagging or sleeve without any
direct contacts between the pipe and the framework.
- Thermal expansion
As the lineal thermal expansion rate of PB pipe is
approximately 13mm for every 10°C temperature
change for each 10 metres of pipe, care must be taken
with the installation to allow for this potential
movement of the pipe. PB pipe should not be pulled
tight between fixed points as this will prohibit
movement if the pipe contracts, and result in excessive
tensile forces on joints and fittings. Allow 10mm slack
per metre of pipe. Expansion can usually be
accommodated by the pipe’s flexibility.
Allow 10mm slack per metre of PB pipe
for thermal movement.
- Chases, ducts or conduits
As per AS/NZS 3500 Parts 1 & 4 or Local Authority
requirements.
Pipes in chases shall be continuously wrapped with
an impermeable flexible material.
Ducts shall be fitted with removable covers.
Pipes embedded in walls or floors shall comply with
the requirements of the appropriate building authority
and/or local regulations.
- In concrete slabs
PB pipe may be installed under concrete slabs in
accordance with AS/NZS 3500 Parts 1 & 4, or Local
Authority requirements.
When PB penetrates the slab it shall be at right angles
to the surface of the slab and shall be lagged with an
impermeable, flexible plastics material of not less than
6mm thickness for the full depth of the slab
penetration, that is, PVC conduit or pressure pipe.
- Clipping and supports
The use of pipe clips should be in accordance with
AS/NZS 3500 Parts 1 & 4 and in keeping with good
plumbing practice. The following table is based on
AS/NZS 3500.
Clips on fittings should only be required where the
fittings are obviously stressed. The installation of pipe clips and brackets is only
to give the pipe support and an acceptable appearance.
The pipe clip must not constrain the pipe diameter and
should allow longitudinal movement of the pipe.
The use of pipe clips
| OD ** | Horizontal or graded pipes | Vertical |
18 mm 22 mm |
600 mm 700 mm |
1200 mm 1400 mm |
** NOD = nominal outside diameter
- Corrosive environment
As per the requirements of AS/NZS 3500 and/or Local
Authority or Regulatory requirements, PB pipe and
fittings installed in potentially corrosive environment
must be protected, i.e. marine environment.
Solar Hot Water
As solar hot water systems are an uncontrolled heat source,
temperatures in excess of 75°C are frequently experienced.
To ensure that the supply temperature is maintained
well within the normal operating temperatures of
polybutylene pipe it is recommended that:
- In additon to the normal valves required for the
system, an adjustable tempering valve (e.g. RMC
Heatguard Solar HP or HF or similar) should be
installed directly at the solar water heater.
- As per AS/NZS 3500 Part 4.2, one metre (1mtr) of
copper pipe is then required before connecting to
polybutylene pipe. The copper pipe can be used to
penetrate the roof into the roof cavity.
- The tempering valve can then be adjusted to
its maximum temperature (up to 65°C depending
on model) by following the manufacturer’s
instructions. This is typically done by removing the
adjusting knob locking device and resetting the
temperature.
- Individual tempering valves are then fitted as
required to control water supply temperature to the
wet areas in accordance with AS/NZS 3500 Part 4.2.
Testing
Testing procedures as required by AS/NZS 3500 part 1,4 & 5 and/or any Local
Authority or Regulatory requirements.
While the system is under test, all joints and fittings
should be inspected for leaks and to ensure that
the pipe has been fitted correctly and crimped
in accordance with
Polybutylene
Plumbing System Installation Guidelines.
Fire and excessive heat
Avoid hot sources continuously above 60oC:
- Keep PB pipe a minimum of 500mm from sources of
high heat such as heating appliances, flues, vents etc.
- Keep PB pipe 1500mm from slow combustion type
stoves, vents and flues used to heat domestic hot water,
wet back boilers etc.
- PB pipe should not be positioned closer than 150mm
to gas or central heating vents, nor located in any
confined space containing appliance vents or flues.
- The primary flow
and returns on appliances such as
slow combustion stoves or room heaters with water
heating coils, wet back boilers, should not be
installed with PB pipe and fittings. (PB pipe and fittings are designed to meet the normal
operating temperatures of domestic hot and cold water,
but not uncontrolled heat input. For these consider tempering valves.)
- Where PB pipe penetrates fire resistant
construction, the fire resistant integrity of the
construction must be retained. Refer to the local
building code.
Protection of PB pipe
For protection of PB pipes:
- If a system is to be exposed to sunlight beyond normal
construction periods, the pipe should be protected
from sunlight (UV) damage.
- When installing, allow for lineal thermal expansion rate of
approximately 13mm/10oC temperature change for
each 10 metres of pipe.
- Leave 300mm minimum space between PB pipe and
recessed electric light fittings, as light fittings are
normally changed on a regular basis.
Product range
PB piping includes:
- 18mm and 22mm pipe in 5m lengths and in 25 and 50m coils
- lagged pipes (pre-insulated pipe for hot water)
- 3 colors with printed descriptions
- straight joiner, reducing joiner (22x18mm)
- M&F adaptors, Cu to PB flared adaptor,
- F swivel connector, bends, F swivel bend, M&F wing back elbow
- Tees, reducing Tees, Cu to PB Tee, wing back Tee
- M&F brazing tails, hose plate, crimp rings, test plugs
- pipe/tube clips for masonry and anchor nails, twist shank nails and Tek screws
- Breech range, sink/bath/shower for floor, side & top entry,
- pipe cutter, crimping tools with replacement parts
As time passes, new parts may become available.
Modern Plumbing - A Hidden Danger
This article is vague since it does not define its use of the word plastic. Does its 'plastics' include PB or any of the other latest products ? Have those problems been overcome ?
Realty Insurances Limited is an independent intermediary, authorised and regulated by the Financial Services Authority, and
is entered on the FSA register (www.fsa.gov.uk/register) under reference 307515. Registered Office: 58 Davies Street,
London W1K 5JF. Registered in England No. 482966
Here is its report of July 2008, as published on the Internet.
Many property insurers have seen a significant
increase in damage and costs arising out of
claims as a result of an “escape of water”. The
resultant damage can be as disastrous as a flood
or a fire.
Traditionally, “escape of water” claims were as a
result of bursts following frozen pipes; however,
a new trend seems to be developing. In modern
water systems, it is increasingly common for
plumbers to utilise plastic pipes and/or plastic “push fit” joints and
connectors. The attraction of such fittings is their ease of installation and a
resultant reduction in cost.
Recent experience, however, points to the fact that there may be a hidden
future cost, as it appears that the modern plastic installations are less robust
than traditional methods leading to a higher frequency of water damage claims.
The traditional plumbing method of using metal piping (usually copper) and
soldered or compression joints seems to be more substantial than the modern
plastic alternative. Pressurised water will always put weak spots under
additional stress and often plastic joints have been found wanting and unable
to cope, with the result that they become detached.
If a pipe develops a leak or a joint becomes detached whilst a property owner
or occupier is away from the premises, very significant amounts of damage can
occur in a relatively short period of time. As much as 300 gallons of water can
escape from a 22mm pipe in as little as 10 minutes, leading to disastrous
consequences.
Many of the worst insurance claims occur when water escapes from the upper
floor of a high-rise building. Water will always find the route of least resistance
and will cascade down stairwells, lift shafts and service ducts. This will, of
course, lead to damage being spread throughout a building and the water
eventually emerging far from its original source.
For commercial property owners or occupiers, it is advisable to have in place a
business continuity plan, should the unthinkable ever happen. The plan should
enable the business to respond quickly in the event of disruption and be up and
running again as quickly as possible.
The plan should be updated on a regular basis and tested to ensure that what
is on paper actually works in practice. For example, one organisation
discovered that there was no reception for their emergency mobile telephones
in the office that was to be used by their senior management team as their
temporary head-quarters!